I am using Citect HMI and a WAGO PLC (750-842) communicating using MODNET (MODBUS over TCP/IP) and have the following problem:
I can successfully define DIGITAL tags mapped to the internal memory of the PLC which starts at MODBUS address 12289.
However, I now need to pass BYTE and/or INTEGER data and have been unable to do this other than by creating a bitmap of tags and declaring the address range in the PLC as BYTE or WORD as required.
Whenever I try defining a BYTE or INTEGER tag mapped to the PLC, the compilation fails with the error message: "Bad raw data type". :confused:
Any suggestions?
Iain
According to the modnet driver the only data types you can have are the following, thats why you are getting bad data type as it does not allow it:
Data Types
Address Format
CitectSCADAVijeo Citect Data Type
DIGITAL
Output Coils
000001 to 65536
DIGITAL (Note: Leading zero is required.)
Input Status
100001 to 65536
DIGITAL (Read Only)
INTEGER
Input Registers
300001 to 65536
INT / LONG / STRING / REAL (Read Only)
Output Registers
400001 to 65536
EXTENDED REGISTERS
(6xxxxx range)
Ef:[r.b]
where:
f = file no. (1 - 65536)
r = register no. (0 - 65536)
b = bit no. (1 - 16)
Thanks! :geek:
At first I was confused by the apparent address range from 6 digits to 5 (400001 to 65536) but when I put that together with the note regarding the leading zero and assumed that the 4 was also a leading character, giving a range of 400001 to 465536, it all worked fine.
Iain
Is there any way to access the disk I/O variables in citect V5.5, there is one tag available in the variables.dbf and it is defined as disk I/O...
1,778
Hi guys! I encountered an error on vijeo citect HMI. The system is configured as main and standby HMI. I have this error on standby HMI, "ERROR...
6,963
I’m using HMI/Vijeo Citect and I want it to take care of some calculation, not the PLC. How to do that, how do I let the Citect constantly make...
1,770
Hello All I am in the process of rebuilding several older PC 133 Ann Arbor 7000 Terminators,running Citect 5.1.Do you think that reducing the swap...
1,715
I am developing a project using Citect HMI and am wondering if it is possible to remove or hide the white border around the last clicked object on...
1,699