Hi All,
I have a contrologix system where i want to create a module fault if any of the module fails in the chaisis.
I have used a GSV instruction to featch the status of Module connection.
But when i remove the module i do not get module fault error.
I even dont have IO eror on PLC IO LED .
Please let me know how where i am wrong.
scan.plc
I have never seen an instance where the ControlLogix did not detect an "owned" module being removed from the chassis. Are you certain that you haven't inhibited the module connection ?
Could you post more details about the module, the chassis, and the network that you are using ?
In addition to the GSV, you would have to verify specific bits of the returned value.
An alternative could also to use a MSG instruction and monitor the .DN bit.
SCAN.PLC said:
Hi All,
scan.plc
Is the I/O local or remote?