CLX connection to SLC via ControlNet
jmcadoo
Apr 2006
Knoxville, TN
Trying to perform scheduled ControlNet connection between 1747-SCNR/A FW Rev 1.4 and 1756-L55/A !756-M12/A Revision 12.25. Following example in App. Note A20389. RSLogix 5k version 12 1756-CNB 5.044 Build 030.
Created generic profile for the 1747-SNCR per the App Note. When finished the Module Properties- Module Info dialogue box shows "Status = Faulted" and "Module Identity: Mismatch".
RSnetworx for Controlnet 4.11 shows both nodes on the network. View > Connection Status in Scanlist Configuration Tool shows the connection as "Connection open is pending"
Any suggestions? Thanks
The error means what it says; the configured connection to the 1747-SCNR doesn't match the actual identity of the device at that node on the network. Maybe with a Generic module it can't match the identities.
Try turning off Electronic Keying on the connection.
Trying to perform scheduled ControlNet connection between 1747-SCNR/A FW Rev 1.4 and 1756-L55/A !756-M12/A Revision 12.25. Following example in...
4,107
Hi all Long time lurker, new member. I have a problem with at little project at home. I have a Siemens Multi Panel MP277 and a 1756-L55...
1,066
Hi, I´m getting that error when trying to connect to the PLC with logix5000. Whow may I reset this error? I it impossible to access the...
1,744
At work I have a Backplane with a ControlLogix Processor, 1756-ENBT Ethernet card and a PanelView Plus all connected to a switch located in the...
4,604
Hi All, I have a contrologix system where i want to create a module fault if any of the module fails in the chaisis. I have used a GSV...
2,639