CLX ControlNet Schedule lost
Lovell
Feb 2013
Saskatchewan, Canada
120
I was troubleshooting an apparent loss in communication between a 1756-CNB and a ControlNet module (plugged into Brabender Controller). I observed no communication updates from the device to the PLC. Also the device did not respond to the commands from the PLC - this unit was working previously. I checked the Comms light on the processor and it confirmed 'I/O OK'. After trying a module reset without any success I decided to play with the RPI time changing it from 20 ms to 40 ms. As soon as I applied this I got the "Connection Request Error. Connection not scheduled." then I also started getting "Resource Unavailable". I cannot Reschedule ControlNet at this time as there are other processes running which I cannot interrupt. I changed the RPI time back to 20 ms but the connection remained unscheduled. Has anyone experienced a ControlNet device becoming unscheduled when the RPI time was changed? Is there a way to re-establish previously existing and scheduled ControlNet connections without going into program mode?
I'm trying to set up a MSG path between a CLX processor on ControlNet to a PLC-5 processor on DH+ and I cannot figure this out. The first attached...
1,296
I'm going to be doing a project and need 24 120 VAC inputs and 16 relay outputs. On Point I/O I was going to use IA4 and OW8 modules. On Flex I...
3,757
I have CLX Processor using Controlnet, I have 7 remote Point I/O modules everything is fine on the Controlnet network, But when I go to save the...
1,510
Trying to perform scheduled ControlNet connection between 1747-SCNR/A FW Rev 1.4 and 1756-L55/A !756-M12/A Revision 12.25. Following example in...
4,107
4,497