Codesys Ethernet IP Scanner - Won't connect to a Wago 750-353

theColonel26

Lifetime Supporting Member
Join Date
Feb 2014
Location
West Michigan
Posts
785
Codesys Ethernet IP Scanner - Won't connect to a Wago 750-353.

The Ethernet device and the Ethernet IP Scanner are both running.

but then I go in to the 363 Device and it says "Adapter not configured yet"
But I configured the I and O data lengths, and the connection string IDK what else I would configure.

2022-07-07 18-03-59.png 2022-07-07 18-27-00.png 2022-07-07 18-25-50.png 2022-07-07 18-39-21.png 2022-07-07 18-11-41.png
 
Last edited:
It is great you figured this out. Sorry I did not see the post earlier. The diagnostics was telling this very clearly the T->O (target to originator), in other words the produced data from the adapter to the PLC, connection size was incorrect.

2022-07-08_Codesys.png
 

Similar Topics

Does anyone in the community have some experience to help a novice understand how to use the Configuration Assembly data for an Adapter device...
Replies
16
Views
7,884
Hello. I need to connect an EtherNet/IP adapter to CODESYS RTE. I have confirmed that the adapter works with Rockwell Logix, and not only the...
Replies
7
Views
2,420
Hi everyone, I am using Codesys for the first time (V. 3.5 SP16 Patch 3) and I have used only Allen Bradley before this. I am struggling to...
Replies
17
Views
4,670
Hello everyone, I'm currently working on a project where I have the RPi set up as an Adapter with Codesys and the Allen-Bradley PLC as Scanner...
Replies
6
Views
3,320
Hi, I would like help if possible with a little problem. I'm using a TM251MESE from schneider electric with Somachine 4.1 sp2. I'm trying to...
Replies
0
Views
2,040
Back
Top Bottom