Comm Auto Dir EA1 HMI to fixed SLCL40A
lesb
Sep 2002
Does anyone know if and the protocol for communications between an HMI from Auto Dir (EA1-S6MLW) and an A-B fixed processor (1747-L40A). It works on the 5/02 to 5/04 fine but can't get it to work with the fixed and autodirect tech support didn't know on the fixed.
Thanks for any advise
If it works with a SLC5/02 then it should work with your 1747-L40A as both only support DH485 protocol.
Check the baud rate and node address as they can be changed.
hi to all, have anyone tried to communicate Schneider PM800 to a ML1400 through rs485? i am having an issue with it just receiving message...
51
Hey guys. As the title suggests, I need to configure a Danfoss Aquadrive FC202 inverter, so that its logic inhibits the local command when the...
90
Hi; In a cabinet of a machine, a Fatek PLC with an Ethernet communication card is working. In the same cabinet, there is a 1 kW inverter. When...
575
After updating a panel, I inherited another PLC for my "learning lab". It's a Modicon TSX Micro. I've not worked with a Modicon PLC yet, so I...
172
Guys need a bit of help getting the instance correct for a 22comme with a PF40P. Trying to get 2 things first is the drive current amp draw...
105