Good day
I have to make ethernet communication between S7-1200 ( 1215c) and Beckhoff PLC CX5010.
My question here any expert can guide me how can I establish communication between 2 different systems in order to I need to read data from beckhoff PLC.
I would see what common protocol is available in each of the PLCs. Modbus TCP is a protocol that I know is available on each device.
Determine the Client (Master) PLC. This will be the one asking for the information from the Server (Slave) PLC.
Here is a link for the S7-1200 acting as a Client:
https://support.industry.siemens.co...bus-tcp-ip-protoclol/85363?page=0&pageSize=10
Here is a link for the Beckhoff Setup:
https://infosys.beckhoff.com/english.php?content=../content/1033/tcmodbussrv/html/tcmodbussrv_configuration.htm&id=
Here is some good information on the Modbus TCP protocol:
https://www.rtaautomation.com/technologies/modbus-tcpip/
Hope this helps you out.
Regards,
Thanks for your reply.
for Beckhoff protocol they write these information about Communication :
The EtherCAT protocol is optimised for process data and is either transported directly in the Ethernet frame or packed into UDP/IP datagrams.
So can I use UDP/IP communication and what is the best way to establish the communication
There should be a Fetch/Write function block in CoDeSys. Wago has one so Beckhoff should too.
Good Luck,
Yosi
I believe EtherCAT is available for the S7, but I have not done anything with this protocol.
Regards,
The 1200 doesn't support EtherCat, at least natively. It's possible that someone made a block for it somewhere, but you won't get deterministic control it off any user TCP communications.
The 1200 supports Profinet as it's main IO bus. Profibus is an option via a comm card. As mentioned above, Modbus TCP it's supported natively, as is generic TCP or UDP packets.
You might need a protocol gateway. Anybus makes a bunch, Hilscher's nettaps are pretty flexible as well.
Hi all I have micro logix 1200 and automation direct panel (EA9-T6CL). I have downloaded .RSS file in micrologix 1200 using 1761-CBL-PM02...
1,804
Developing Communication between Energy Meter(Indigo+ Schlumberger) & SIEMENS S7-1200 Hi Members, I am Currently facing a challenge regarding...
1,491
problem in communication between micrologix 1200 & Panel View 600 Plus by serial DF1 Hello Friends i have to do communication between micrologix...
6,618
Hi ! Everybody ! Please..help me about communication between S7 1200 and inverter or any varispeed inverter had MODBUS support by module CM1241...
20
11,176
:yakyak: :bow: Reported Issue : Siemens HMI does not Communicate with Siemens1200 PLC. Sequence Of Events : Checked status of HMI and PLC and...
5,438