I have one CJ2H-EIP21 PLC with an ethernet hub connected with some devices. There is another CJ1 PLC with ETN21 module also with a hub connected with some devices. Now I need to set up communication between these two PLCs. These two PLCs have difference IP address. what is the best way for hardware? Will I need a router in between? Can I just use a ethernet cable plug to both sides of the hubs? What is the best way for software? Will I have to use FINS communication? Will I need to set up routing table? THX
post the ip, subnet and gateway for each plc. if they are in the same range then you can use a cable to connect them. if they arent I would put them in the same range if possible.
Thanks diat150, Because they are both kind of alone, Can I set up both same as 192.168.0,1, subnect 255.255.255.0? So you mean I can just plug cale to hubs? what about software? FINS is the only method? THX.
If you can set both IPs like (1)192.168.0.1,(2)192.168.0.2.
From that point it is easy
You will need routing table for both of them with the same network No.
If you can set the IPs I can send you working sample.
I send you 2 projects
Your lucky I document my projects in English.
Pay attention both set to network 10
You need to use routing table(not Attached)
I use to read not to write when I deal with communication .So both of the PLCs just read from the remote PLC.
Feel free to ask if you have any question.
I have been asked to design a control system of which will have 24 winder stations. Each winder station will have its own control system of wich...
1,938
Hello everyone, I just started a new project but want to make sure I am heading to a correct direction before I am too far down the...
3,995
Hello All, I am just starting to learn how to communicate with HMI's (Total Control Quickpanel/Proface) and some guidance would be very helpful...
5,620
Dear, I was reading something concerning OPC follows the data transmission between the PA(control system level) and the PLC will be based on OPC...
1,888
Hi I have a PV plus (latest firmware) programmed using FactoryTalk View Studio 8. After downloading the runtime file, I am getting the following...
6,731