Compact Logix and Siemens TP170B Communication
vaghuan
Jun 2012
Bangalore
Hi
Im using Compact Logix L32E PLC and Siemens TP170B
HMI using Win cc flexible.How to communicate between this two?
There is no Ethernet port in the panel as well as in Wincc the CPU name is not found.
I tried to communicate from CH0 using DF1 and DH485
that also not worked.But CH0 flashing green.
I want to know how to Tag the address in HMI corresponding PLc
For Eg In PLC --- Local 2:O Data 0 HMI:????
Please help
It should be possible to use the DF1 protocol in the TP170B project.
You need a null-modem cable between the TP170B and CH0 on the Compactlogix.
Be sure to have the same settings for the serial port on both sides, baudrate, stop bits, error check.
If you have a green flashing CH0 LED, then it indicates that at least the TP170B is attempting to communicate with the compactlogix PLC.
This is where it gets fishy. I think (not 100% sure though), that the tags in the compactlogix must be formatted in PLC5 style for the TP170B to be able to read and write tags. I dont have personal experience, but this is how I understood it.
Looking for feasibility and ideas on how best to pull some signals from a Siemens 6EDI 052 IMD00 0BA6. My facility is 80% Rockwell based, a small...
1,703
Hi there, Can anyone suggest the solution to communicate between AB Compactlogix L36ERM controller(Which is having remote flex IOs over ethernet)...
3,697
Hi , has any one encoumtered the following problems when working with simovert masterdrive connected through profibus to compactlogix using...
3,344
Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
98
gents, I am trying to configure communication with EMERSON PK300 controller through port A1 using generic ethernet communication module . I could...
112