I've got an AB Compact Logix L32E processor. I'd like it to talk to a Zumbach 8100 Capactitance Gauge using Ethernet.

Unfortunately the Zumbach doesn't understand any protocols except it's own.

I can set up hyperterminal to talk to the Zumbach over ethernet.

Using HostAddress 10.255.10.55 and Port Number 100

Connect using TCP/IP (Winsock)

From Hyperterminal, I type: d8000<cr><lf>

and the zumbach replies with d8000 3.26<cr><lf>

How do I set up a message instruction in the compact Logix to communicate with this device?
 
You will have to use ascii strings to communicate in the case.It can send out ascii strings over the serial port.
Look at the help files in RS5000 or the AB web site.

That 8000 command that you send from hyperterminal sounds possibly like it might be using a Modbus protocol. If so there is a modbus module that you could purchase.
 
This is not Serial... It is Ethernet.

There is a Prosoft module that AB claims could do the job.

That's not an acceptable answer. I'm planning on building about 50 enclosures each with it's own PLC.

I'm trying to make the decision whether to go Siemens or AB.

And I've let my Siemens and AB vendors both know that they have to prove that they can talk to the Zumbach without using an extra card.
 
For logix platform you must use an additional module, controller can't do RAW ASCII directly
In addition to prosoft module you can use 1756-EWEB / 1768-EWEB modules and write own protocol using Open Socket interface
 
Last edited:
I'm looking at using Compact Logix ... Not Control Logix...

However, Siemens says they can do it real easy through there PLC with no additional hardware.

If I can't do this with the Ethernet port on a 1769-32E, then I'll probably go Siemens.
 

Similar Topics

In the few examples that I have seen on AB's website, the MSG instruction is triggered continuously; as soon as it's done, it is re-triggered. It...
Replies
5
Views
1,545
I am having trouble getting a MSG instruction to work. My PLC is a 1769-L24ER. The other PLC is a 1768-L43 with a 1768-EWEB/A comms module. I...
Replies
0
Views
2,199
I have an issue with the communication trough the MSG instruction, I want to send information to a printer from a 1769-L35E, I have configured the...
Replies
17
Views
16,117
Does anyone know if is possible to read data out of a ProfaceHMI/PLC into a CompactLogix PLC? I have a bunch of OEM machines on our plant floor...
Replies
2
Views
496
Hey Guys Having some trouble again with message path, I thought I had these figured out but I've not been able to get this one working. I...
Replies
4
Views
593
Back
Top Bottom