conductivity to consistency
garby
Jun 2003
Shanghai, China
Hi there,
I am using E+H CLD132 sensor to detect the conductivity of both NaOH solution and HNO3 solution, I can only read the conductivity with unit ms/cm, now the end user asked for the data of consistency with unit %, can I change the data of conductivity into consistency in %? how?
i saw some one applied a linear function into this transition, but the result is not satisfied.
thanks and best regards,
Are you reading the 4-20mA output from the CLD 132 with a PLC or a 4-20mA indicator? If you are, you can convert the ms/cm to % with the help from the Lab. The Lab can make a solution with a known % of NaOH etc. If you measure the conductivity of the sample, you know that X ms/cm = Y%. I do this all the time in our CIP's.
thanks nonuke!
yes i am reading 4-20ma output with s7-300 plc. i've tried the lab, but the result is not satisfied. for example, i measured 204ms/cm for HNO3 with 1.6%,25 centigrade degree, but when I measure the solution with 1%, i got 145ms/cm, according to the calculation, it should be 128ms/cm.
this is also for CIP project for a dairy plant
In most Dairy plants we build CIP's for, the % of NaOH and HNO3 is kept the same over the years, or than the change is very small so your set point will always have the same % (you will never use a 0-100% scale). You are correct, the change in conductivity is logaritmic not linear.
Our process is:
NaOH for example,
SP1: normaly 2.0% , above this setpoint, the clean is ok, and the timer is running, below the setpoint, the timer is hold;
SP2: normaly 1.5%, below this setpoint, the solution will be drain, above this setpoint, the solution will go back to the lye tank;
SP3: normaly 0.1%, below this setpoint, the flow will go to the water recover tank to save the water;
current i can only use ms/cm, but customer would prefer %
thanks,
garby
Hi garby: Just ask the Lab to make a sample with 2%, 1,5% and 0,1% of NAOH, than you can insert the conductivity cell in each sample and find out the conductivity for each percentage.
Hi All, We are looking for a new paperless recorder, our current ABB SM1000 is on its way out, the screen is difficult to see. There is a long...
2,563
Hello, I have a Suntex EC-410 Conductivity controller that feeds a 4-20mA signal back to a compactlogix. I have the manual for this device but no...
1,333
I've been asked to build a "simple" salinity monitor / controller for a chilled brine system. To simplify things, the owner prefers a tank-mounted...
1,959
Hi Guys I need a bit of help here with my math! I have to measure the conductivity of caustic in a line. Now what I have been given by the...
3,606
I'm trying to get the measured conductivity from an Oakton CON2700 conductivity meter into a PLC. The unit has an RS232 output for a printer...
2,359