Connected Components Workbench Analog Output Programming Trouble!!
Dec 2017
Seattle
Hi all,
I'm having trouble programming the analog output on my Allen Bradley Micro850 with OF4 extension. I enabled the channels, minimum-maximum output range 4-20mA, with the data format in engineering units. I'm trying to control an inverter wired to a motor. I used the MOV instruction block to assign my analog output with values from my analog inputs, but it seems that the analog output does not produce any signals (tried with my multimeter) even though there are values in CCW's live mode. Does anyone have the solution for this?
Thanks,
-Grant
Hi all,
I don't think the output is suppose to be a signal that you can measure with your meter! According to the global parameters for the OF4 output it is an "INT" value. So to me this would probable a 16 bit word value just as if you was reading a Modbus Address Value.
I don't know how the inverter will interpret that value.(I don't know how you would be communicating that value to the inverter??)
Now if you are communicating to the inverter with modbus all you would have to do is MOV that output to the modbus address for let's say speed and the inverter would respond according to the word value in the output.
Now I may not understand anything that you are trying to do, so if I am way off base please forgive, and just disregard this post!
was trying to use Connected Components to connect to a 525 drive via usb with the face off but can't seem to connect to it. the screen lights up...
792
So I'm using CCW to program a panel view and this is not my first I have done many. My Problem is I get an error message that I have never seen...
499
How do you expand a branch in connected components workbench. Example i want to add an interlock around more than one contact. Most software you...
1,282
I’m working on a conveyor project for work. We’re trying to install a few diverts to carry product directly to one of two trailer doors. I have...
1,058
I cannot get CCW to add a controller, i keep getting a error message saying that the device is not authorized. This happens with any model and...
1,374