Hmm, the 5/04 has a RS232 port that can be configured for DF1 or DH485. You might be able to use a 1761-NET-ENI on that port. Not sure what a 5/05 costs these days, but you might not be that far off from the cost of one.

The other ports on it are DH+, it will likely be a lot more expensive to convert DH+ to Ethernet than the 5/05 costs. The most common way is a ControLogix Gateway, which consists of a 4 slot CLX rack, power supply, ethernet module and DHRIO module. You'd be into a few grand for that solution.

Seems like this might do the trick:
https://www.anybus.com/products/gateway-index/anybus-communicator/rockwell-df1-(rs232-422-485)

Edit: or this:
https://icomtechinc.com/serial-conn...AfGmGEt9V5H57W1J7gN3BWVL714rlKFhoC14cQAvD_BwE
 
Using the USB to serial port option is interesting. I was unaware of that option.

But, in a lot of cases, the serial port is taken for use with a drive or other device. I was thinking about a DH+ option.

The price for a new SLC 5/05 right now is over $12,000 USD.


I have seen some adapters available. But, was hoping someone with some experience with one of them would chime in.

There are 2 that I recently discovered. But, have not used yet. Prosoft AN-X2-AB-DHRIO and the Automation Networks anc-100e
 
Last edited:
This is great news, more cost effective for upgrading from PV550 to PV+7 on an Slc5/04. We had been using Prosoft An-X2 units for this, but they were expensive.

You definitely couldn’t use a USB lead until recently as I enquired with RA.

Looking forward to having a go with a serial connection now
 
Last edited:
What do you need to know? a DH+ gateway sounds like it would work, see below for the one we sell

https://www.plccable.com/ethernet-i...ighway-plus-dh-gateway-converter-ethernet-ip/
I find that gateway device interesting.
A problem we have with existing legacy PLCs and OPC applications, is that some of the data is sent from the PLC by unsolicited messages to the OPC server.
Does this device support that ?
I checked the manual, and there is an address mapping feature so you can setup for data that is to be sent from an HMI to a PLC, that you can specify that the data sent to a specific IP address is forwarded to a specific DH+ address.
Does it work the other way, from PLC to HMI/OPC as well ?
 
I find that gateway device interesting.
A problem we have with existing legacy PLCs and OPC applications, is that some of the data is sent from the PLC by unsolicited messages to the OPC server.
Does this device support that ?
I checked the manual, and there is an address mapping feature so you can setup for data that is to be sent from an HMI to a PLC, that you can specify that the data sent to a specific IP address is forwarded to a specific DH+ address.
Does it work the other way, from PLC to HMI/OPC as well ?

Here is a paper on a Matrikon OPC server that may have the answer

https://*************************/w...MI-feature-on-a-Data-Highway-Plus-network.pdf

There are more application notes at the ANC website https://*************************/automation-networks-anc-100e-2

I will ask their tech support and see if I can get an answer, if you were closer I could send you a demo to try

EDIT: Looks like Phil is blocking them
 
topiasl
It is still there, but as noted in my original post you need a TechConnect contract to be able to view it. Search for QA29511 after you log into the Knowledgebase.
 
Last edited:

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
89
Hello all! Can someone shed some light on this? I am trying to connect a PVP 6 to a PLC-5/30 through the serial ports because the old touch...
Replies
2
Views
538
Hi guys Just a thought I have a pvp on a 192.168.1.xxx network if I wanted to add a the screen to a second network say 192.168.0.xxx could I...
Replies
2
Views
1,383
is it possible to comunicate a powerflex 753 (ccw) using ethernet 20-750-ENETR card to a panelview plus 6 1250 (factorytalk view studio me)...
Replies
0
Views
1,495
I am trying to set up a PV+ 1000 to monitor plant wide processes. I am not having any trouble setting up the Control Logix and SLCs that I have...
Replies
13
Views
6,657
Back
Top Bottom