flyers Member F Join Date Sep 2006 Location Amk Posts 295 Apr 6, 2007 #1 HI guy, One of our customer is running ControlNet (with ControlLogix), he wants to connect a spare unit of 1305 AC drive to work with a motor. What is the accessories required to do so? Can someone please recommend? Thank you.
HI guy, One of our customer is running ControlNet (with ControlLogix), he wants to connect a spare unit of 1305 AC drive to work with a motor. What is the accessories required to do so? Can someone please recommend? Thank you.
mgvol Member M Join Date Dec 2004 Location Knoxville, TN Posts 746 Apr 6, 2007 #2 Look at the AB 1203-CN1. Here's a link to the user manual: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1203-um012_-en-p.pdf
Look at the AB 1203-CN1. Here's a link to the user manual: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1203-um012_-en-p.pdf
flyers Member OP F Join Date Sep 2006 Location Amk Posts 295 Apr 6, 2007 #3 mgvol said: Look at the AB 1203-CN1. Here's a link to the user manual: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1203-um012_-en-p.pdf Click to expand... Hi, Basically I just need a 1203-CN1 & a T-Tap CNet cable?? Thank you for your info.
mgvol said: Look at the AB 1203-CN1. Here's a link to the user manual: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1203-um012_-en-p.pdf Click to expand... Hi, Basically I just need a 1203-CN1 & a T-Tap CNet cable?? Thank you for your info.
mgvol Member M Join Date Dec 2004 Location Knoxville, TN Posts 746 Apr 6, 2007 #4 You will also need a ScanPort cable to connect it to the 1305 drive. Refer to page 2-2 in the user manual for a list of ScanPort cables and ControlNet taps.
You will also need a ScanPort cable to connect it to the 1305 drive. Refer to page 2-2 in the user manual for a list of ScanPort cables and ControlNet taps.