I tried to search the forumn for topics related to "first Out" alarmingm but didnt have much luck.
I noticed V16 of Logix5000 can somewhat support "first Out" alarming? Has anyone used this, or had any luck with it?
I have a number of digital inputs, through a few 1756-IV16 cards, that need to be monitored. The customer only tells me they want local "first out" annunciation. From what ive read, the rolling timestamp will only update per I/O card, as a whole (ie. I cant use the time stamp for two different inputs on the same card, to determine which input actually tripped first.)
I see Knowledgbase has a sample program for 5 inputs on a Logix500 platform.
Can anyone shed light on how this can be done on a Logix5000 platform. Or if anyone has any luck with the new alarm features of Logix5000 V16 - and if its a true "first out"?
NH
Heres the logic i use, its negative logic based. Once the bits are mapped, its fast. You can mask in and out the alarms you want, so setting up multiple sections of a plant from one main latch file is also simple. Overkill for 5 alarms, but it works
Ghetto,
If you have 2 or more PLC scans to determine your First Out, then it should work just dandy. I find that most systems have 5 or 6 scans before relays drop out, or another switch changes state, so a First Out WILL work well. Maybe not 100%, but good enough to make it worthwhile.
Yes, if more then one input changes on a single scan, then you will not be able to find the proper firstout. It will flag the first firstout it finds. It more used for a trouble shooting tool then any thing
Ghetto,
Am I understanding you corrcetly, that it is not possible to catch "first Out" on the same card, if more than one input changes?
from nhicks:
Am I understanding you correctly, that it is not possible to catch "First Out" on the same card, if more than one input changes?
actually it IS “possible” ... it’s just not 100% GUARANTEED RELIABLE ...
the simple reason is that the individual input devices built into the card do NOT all share exactly the same electrical characteristics ... specifically, some may react faster or slower than the others ... so if two or more inputs electrically turn OFF at the same time, there’s no way to guarantee that the PLC will see - and record - the bit status correctly ...
but don’t take my word for it ... experiment and prove it to yourself ... jumper a bunch of inputs together and then turn them all OFF at the same time - and have the PLC record the bit pattern as soon as the input data changes ... you’ll find that USUALLY all of the inputs will operate simultaneously - but NOT always ... it’s a random thing ...
the major idea is that a PLC-based “first out” tester MIGHT be fully adequate for your needs ... if it is, then party on ... on the other hand, you need to be aware that such an arrangement might occasionally give incorrect results ... just be aware of that potential limitation - and take action accordingly ...
273
hi all, i have a plc i need to get info from for a site im working on: I have a 1764 Micro Logix 1500 LSP Series C (See Attached Image) im...
389
I currently have a weird issue involving Ethernet IP communication between a ABB CI873 (EthernetIP Module) and a 1756-L83ES. The Layout is as...
792
Possible for two processors in same rack to have separate motion groups across a single Kinetix Rack using a single EN3TR? One 6500/5700 rack, 8...
436
Hi all! I am hoping to find some help understanding the ABB VFD Connection to my Rockwell PLC. I have set up the VFD parameters based on...
696