Control Logix Redudant Processors and ControlNet Help

reese006

Member
Join Date
Sep 2008
Location
Birmingham, AL
Posts
21
Ok so I fubarded a new system today that has Redudant L72's and ControlNet. I can not get the chassis to sync, even with the processors out and all remote IO turned off. So the chassis only have Enet, Cnet, and RM modules and they will not sync.

Is there a way to start fresh, main thing is how can I wipe the ControlNet Cards schedule?
 
You did not give any detail at all so here are my random thoughts

#1 Verify that all cards are using Redundancy Bundle firmware revisions.
#2 Download the redundancy manual
#3 Clear Keeper resets the modules

RSL
 