Control Logix Secondary Rack Module Status

lijochrn

Member
Join Date
Jul 2015
Location
Seoul
Posts
31
Hello All,

Can you check the below configuration and tell me how to check the module status of modules in the secondary rack of a redundancy configuration?

GSV function is working well for the modules in the PRIM chassis. But the SECONDARY chassis modules are not showing in the IO tree, hence how to address them?

If I need to use the MSG function what should be the
Communication Path?
Class
instance
Attribute

1,1,2,192.168.10.2,1,7 will be fine as a communication path?
or 1,1,2,192.168.10.2,1,XXX,XXX,XXX,XXX?

192.168.10.1 = 1A2 (EN2TR Secondary address)
192.168.10.2 = 2A2 (EN2TR Secondary address)

Red ceheck.jpg
 
Rockwell has a manual and tech notes on redundancy monitoring. It requires message instructions. Look at manuals 1756-um535 and 1756-um015.
 
Rockwell has manual and tech notes on redundancy monitoring. It requires message instructions. Look at manuals 1756-um535 and 1756-um015.

Thank you for the reply.
Both manuals detail the GSV instructions to check the CPU/RM module status.

However my original question is regarding the module status of other modules in the secondary rack. I couldn't find any info for such in both manuals.
Or I missed that part?

Thank you!
 

Similar Topics

I am having trouble with getting no control of my analog output signal. I am using the SCL function block to control my analog output. The logic...
Replies
11
Views
249
hi all, i have a plc i need to get info from for a site im working on: I have a 1764 Micro Logix 1500 LSP Series C (See Attached Image) im...
Replies
2
Views
378
I currently have a weird issue involving Ethernet IP communication between a ABB CI873 (EthernetIP Module) and a 1756-L83ES. The Layout is as...
Replies
8
Views
758
Possible for two processors in same rack to have separate motion groups across a single Kinetix Rack using a single EN3TR? One 6500/5700 rack, 8...
Replies
1
Views
426
Hi all! I am hoping to find some help understanding the ABB VFD Connection to my Rockwell PLC. I have set up the VFD parameters based on...
Replies
4
Views
665
Back
Top Bottom