Rick Campbell
Member
Please help. I'm upgrading a SLC 5/04 communicating with a standard PanelView to a ControlLogix communicating with a PanelView Plus 6. So far I've converted two screens. One works great, but on the other the comms keep dropping in and out and I get messages saying something to the effect that CLX Processor packet disconnected in route, and then I get messages saying tag nnnn now resolved in processor. The kicker is that if I go from this screen to the other working screen, I still don't have comms. The screen with the problem is mainly momentary pushbuttons and multistate push buttons. Most of the tags referenced are arrays of DINTS. I was wondering if maybe array size matters - some 60+ elements. Does the PV request info for the whole array even if the object only looks at one element? Any ideas would be appreciated.