I was wondering if anyone can help me. I am programming an AB Control logix PLC with RS Logix5000. The problem we are having is that when the processor key is turned to the program position and the processor goes out of run mode any bits that are on via the program stay on. This is really frustrating as all the bits that are mapped to the Citect Scada stay on and give a false indication to the operator.
Thanks in advance
Allen
Are you using an SLC processor with a three position switch, run/program/rem program ?? if so, select rem program, this should fix the problem, just keep in mind, any changes that you make will be online
What do you mean by 'Any Bits' ?
Internal bits? Outputs? which?
I'm guessing you mean internal bits, and yes, they will always stay in their last state. As far as I know, the ControlLogix doesn't have a 'Last Scan' flag. If it did, you could use that programmatically to reset all of your bits.
If it is necessary to clear things on a powerup, use the s:fs flag, or a powerup handler.
If you are looking at physical outputs, you can configure in the I/O configuration how outputs behave in program and fault mode (per point). Each point can be set to 'On', 'Off', or 'Hold'. They should default to off, but may have been set to hold.
Does the CLX line support a Status bit of RUNning ? If so, then you could read that status and display it. We do something like that for the SLC-500 series.Allen: You will find that most PLC's keep internal memory bits at the last state when you switch run->program.
Thanks for you advice guys. It is only internal bits I am talking about.I am communicating to the Citect scada using an ethernet module. The only way I can show external inputs and outputs on the Scada is to use alias tags configured in the CLX. So even if the actual input or output is off in program mode (as they are set to off in the configuration mode) the alias tag still shows an on state. I will try to implement Daves idea about displaying a status bit of running on the Scada to alert the operator of the PLC status.
Thanks Allen
269
hi all, i have a plc i need to get info from for a site im working on: I have a 1764 Micro Logix 1500 LSP Series C (See Attached Image) im...
388
I currently have a weird issue involving Ethernet IP communication between a ABB CI873 (EthernetIP Module) and a 1756-L83ES. The Layout is as...
774
Possible for two processors in same rack to have separate motion groups across a single Kinetix Rack using a single EN3TR? One 6500/5700 rack, 8...
432
Hi all! I am hoping to find some help understanding the ABB VFD Connection to my Rockwell PLC. I have set up the VFD parameters based on...
691