Control Voltage to plc tripped
bornwild
May 2010
Riyadh
429
hello everyone
My control voltage (24v) to plc and sensors tripped. I tried to reset the C.B ,it tripped again. the 24 v is goin to 8 sensors and the plc. How do i check which sensor is giving me the problem and causing the breaker the trip. Is there any easy way to check which sensor wires are faulty without having to check each sensor
How do you know its one or more of the senors?
Disconnect all the sensors and see if the breaker stays on.
Use a meter to check each sensor for shorts while they are disconnected.
There are only 8 of them, should be pretty easy to find it.
With power off, put meter in low Ohms mode. Connect across 24DC supply output. Disconnect power lead to each sensor one at a time at PLC. When resistance goes high (maybe 1000 Ohms or more), you found the short.
The problem may be a shorted cable. Rubbing against a moving part, for example. Do a good physical examination first.
@keith.
So should i disconnect the wires which are input to plc and check the resistance ?
PS: needless to say i am fresh graduate.:unsure:
Is the inputs connected to the input card via a removable terminal block? If so just remove the whole lot. If not then power down the system and remove the entire card. The PLC may go to fault but this wont matter for the purpose of the test.
If the power stays on, do what the others have suggested and test each sensor one by one.
If the power goes off the try removing the output card. Carry on like this until you find the problem.
Hello All, I am working with a powerflex 525 trying to get multiple speed references. I got it working on my bench and then I went out to the...
1,100
Hi All. I am trying to commission a Powerflex 525 Drive but currently only have access to +24VDC, I simply want to assign Ethernet/IP Address...
18
7,839
ok, I'm kinda new at this, I have a linear transducer that is analog out 0 to 10 volt, I have a baldor mircoflex (analog in) that I am going to...
1,744
Hi Team I need your advice please, what are the consideration of selecting control voltage levels in a PLC and I have already make my mind to...
2,841
Last night I came across a weird situation at the plant. A hydraulic unit wasn't running, but it should have been. Closer inspection revealed...
16
8,827