I was wondering if any of you have ever tried to control a load using the internal 24VDC on a Powerflex 525. In an application I've been working on, I need to command a solenoid to open when the VFD is told to run. Essentially it's for water on a vacuum pump. There are three such VFDs to control.
As they currently exist, these VFDs are installed in remote cabinets and controlled by Ethernet/IP. As such, there is currently no 24VDC supply in their respective cabinets. We were hoping that we might be able to use the drive's internal 24VDC supply to power the small solenoid through the R1 dry contacts. It appears that the relay has been setup properly, and the solenoid is definitely wired properly, but we get F111 faults when we try to run a drive; they work fine without the solenoid installed and the R1 will operate as intended. I'm wondering if the safety chain detects a small drop in voltage due to the inrush to the load and causes a fault.
I'm wondering if anyone has tried to control a light load using the drive's internal 24VDC supply? Is it possible, or is there something I'm missing?
Thanks!
I wouldn't do this. I don't know what the permitted load on that 24VDC coming from the drive is but it is meant for control power for pushbuttons and 4-20ma (so at least 20mA lol) and I would never expect to be able to do anything substantial with it. What is the current rating of the solenoid?
Can you get a 120VAC solenoid in your vacuum pump and use the dry contact from the drive for that? Or at least a diode across the solenoid contacts to prevent voltage spikes?
According to the manual the maximum load on the 24 Volt control power supply (terminal 11) is 100 mA. I bet you are pulling down the 24 Volt to the point where you lose any of your inputs, hence the F111 fault.
I wouldn't use it to pull in a relay, but we ofter use the internal 24 VDC to power a 4 - 20 control loop.
Really handy when you want a stand alone drive to control pressure etc.
Afternoon all, I'm working on setting up a large excel recipe table for porting updates through the Linx Gateway RTD/DDE function into my recipe...
117
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
512
I'm a Manufacturing Engineer with limited PLC experience and I am doing some research for our Controls Department. Does anyone have experience...
185
Good Evening , I should know more about Solid State Relays . I have a system with 8) 120 vac Vibrators . These Solid State Relays have...
24
2,075
Hi All, I am facing one issue with the SEW MDX61B drive. Issue- I want to run a conveyor with this drive in two directions but it runs in...
347