Good morning all.
I needed some data from another system so I set up a message block in the controllogix to read 3 words. When programming I copied a MSG block pasted into new rung created all the required tags, changed all the attributes in the new MSG block and it worked. Was getting my data. The next day The block I copied had all the atributes that I entered into my new MSG block and the new one was errored out. I cahnged the info back in the old msg block and it was ok. My new msg block however will not work. none of the control bits will toggle and the msg block will not work. Any ideas????
-first thought is check the path to the target processor
-the second is it seems to me the message control tag must be a controller tag. I could be wrong on that though.
-you are messaging similar datatypes?
A screen print could help....
Message type =PLC5 typed read
source= n102:2
elements= 3
destination= N102_2_msg_read tag in an INT (3 deep)
MSG control word= N102_2_MSG_read0
Christoph that looks correct...
I just copied some working CK5K to PLC5 msg's to make it not work. The only thing I found was the CL5K Destination Tag must be a controller tag and must have the [0] after it.
"N102_2_msg_read tag[0]"
I hope that helps....
It sounds like, when you copied and pasted, you did not create a new MESSAGE type tag (labled "Message Control" in the instruction block) to control this new instruction. If you did not then both of the messages, the one you copied from and this one, are trying to use the same controlling element. Each MSG instruction must have its own unique "Message Control".
Ok! It appears my problem was I had the main tag name in the destination and not the first word [0] seems to be working fine now
THANKS FOR THE HELP EVERYONE!
hello i had a 1756-l61 with firmware ver 13.24. a solid red made the processor not functioning. i ordered a processor that came with firmware ver...
3,820
1) I am currently trying to integrate a Prosoft MVI56E-MCM Module into a 1756-L61 CONTROLLOGIX5561 that is a redundant system (CPU is redundant...
3,422
Good Afternoon , We have a ControlLogix 5561 controller. The maintenance group , powered down the machine and lost the program. The battery...
5,127
I am in the process of implementing a PID loop for dosing to a water system. I would like to use an analog input for a water quality sensor as...
1,683
Hi I am new in ControlLogix, so I don't know the details of the scan cycle, I have been checking a couple of programs and I have found the...
1,964