Controllogix 1756-L85E no processor web access

markquinn24

Member
Join Date
Apr 2015
Location
MN
Posts
2
Hey, really simple one likely, but I am unable to gain access to our L85E processor web interfaces. We have flashed these into v.35 firmware which I believe should enable Web interface access.

No projects loaded. Am I missing something obvious? Any help would be appreciated.
 
Make sure you have enabled the controller web page via the controller properties settings or another method. Per the manual they are disabled by default starting in v33.
 
Thanks plvlce!

You know the feeling when you are sure that you have checked all options in the controller settings and the web page configuration wasn't there before you had posted the manual link? Coffee!

Working like a treat now.
 

Similar Topics

We have a project where we have the 1756-L82Es in redundancy with Remote IO Backplant via EN2TRs. Everything works and is redundant but we can...
Replies
2
Views
369
Hi there! I posted few days ago about a fault i had with my motion. I did some cable check and replacement and it didnt solve my problem yet but...
Replies
0
Views
371
Hello, We have a customer with a 1756-L72 ControlLogix PLC. They have recently got a T01:C62 Fault Code. I am trying to figure out how to...
Replies
6
Views
1,050
PN1651 - ControlLogix 1756-OF8/B modules may exhibit spurious channel 4 through 7 faults. Rockwell just released this and we have an upcoming...
Replies
6
Views
1,067
I was wondering if anyone else has had issues with the PA75 bricking on power ups. We had 2 that were a year old brick on us. 1 bricked when the...
Replies
1
Views
860
Back
Top Bottom