ControlLogix fault routines
It is tricky sometimes to deal with faults from a watchdog timer. These are usually, but not always occurring because you are caught in a loop. I'm sure I'm not saying anything there that you didn't know. But here is the catch...
If you setup a fault routine to capture and clear the fault, when it is done it returns you back to the same location you were in before the fault occurred. Again, that is usually back into that same endless loop. If that's the case, it will just fault again milliseconds later since you are still stuck in the loop.
Rockwell made it so that if a watchdog fault does occur, you can clear it via the fault routine. Once. Not twice. So if the controller returns back into the same loop, we will get a hard fault the second time the watchdog timer expires.
Now, if it isn't a loop and is instead just an excessively long scan, then when it returns after clearing the fault, it hopefully will finish the scan and complete that task. Once that task completes, then if another watchdog fault occurs, it will run the fault routine again. So the task successfully completing resets the "counter" if you will.
I'll post an example of some logic I use here shortly.
OG
Here is an example of a simple fault routine in the Logix. I used an emulator as my controller and I was using v28. The included file is the .L5K
After opening it, look at the Controller Fault Handler for the fault logic. There is a UDT used for the fault information. The MainTask just has some logic to cause a Watchdog fault.
OG
Thank you I will download and have a play with an offline processor, when it happens on our system we sometimes have to stop or delay the starting of the PanelView sub routine, so I am thinking that we may have an issue with the PanelView, but it only happens once every few months.
Here’s an example of logging faults from a system I inherited. I have done fault routines in MicroLogix, but haven’t done my own in ControlLogix. I haven’t yet looked at the previous example posted.
7B823B54-4017-477B-BCB5-925A5FDA3EDF.png FC8EB42E-ACC4-445A-BA42-608253C1CCA5.png
Hello, First post here. I am currently interning at a company and learning the ControlLogix System. My project that I am tasked with is...
1,533
Hi there! I posted few days ago about a fault i had with my motion. I did some cable check and replacement and it didnt solve my problem yet but...
373
Hello, We have a customer with a 1756-L72 ControlLogix PLC. They have recently got a T01:C62 Fault Code. I am trying to figure out how to...
1,053
An issue occurred at an organization here in whereby the ControlNet card developed a fault. Card Details: Catalog/Series; 1756-CN2RXT B Part No...
443
:scratch: I have a strange behavior, sometimes Major Fault Type 4 Code 20 occur, I know the reason, I used an array with a word index which can...
23
9,012