Hi Gents,
I am here with an 1756-L73 with a partner 1756-L7SP.
This is for an hydraulic press machine, with an very critical scan.
I need your help to clarify the following:
The values below, comes from the Properties>Monitor in each Task.
The current Motion Scan is 0,5ms, and 10ms for the Base Update Period.
The Safety routine has a scan time of 7ms.
The Continuous and only the task in the code has 42ms of scan time (Main Task).
The System Overhead Time Slice is 50%.
They do not use any Periodic Task.
So, my question is: When is executed the background routines, as communication?
Should be after the Main Routine 42ms, but....I do not know if this can run with System Overhead Time Slice at 50%.
I think that the Main Task ( the only task in the code), it is interrupted several times.
I cannot use the Task Monitor to confirm this above because I am using the RSL5K version 31.
Any help?
:rolleyes:
thank you!
Hi Gents,
Any help?
:rolleyes:
thank you!
System Overhead Time-slice seems to be on the high side, but it can be set high, but make sure that you check the box to run the continuous task during unused time-slice period. That way once all the communications (including I/O data) is done, the controller gets back on with executing your code, rather than doing nothing while waiting for it's time-slice period to end.
I cannot remember the time-slice interval, I think it is every 5mS
Hi everyone: I have a doubt about postscan in RSLogix 5k, for example in help file for OTE instruction, says that in Postscan The rung...
1,208
My new friend Ron Beaufort got me thinking about the issues with using OTL's in regards to a power cycle. While you can use a first scan bit...
4,800
Hi Guys, Quick Question... Is there a method or instruction to purposely delay the scan time of a ControlLogix processor? We're looking at...
4,061
Let's say... A_DINT = 100 In some subroutine: rung 1 : A_DINT = A_DINT + 1 rung 2 : A_DINT = A_DINT + 2 rung 3 : A_DINT = A_DINT + 3 After a...
1,429
Hi guys, I've got a basic question about how the "S:FS" bit is handled in CLX processors. I'm wanting to trigger some anti-diameter reset logic on...
10,689