ControLogix Control net gateway
(8{)} ( .)
Apr 2004
Israel
625
Hello All,
I've got a communications issue with a controlNet gateway.
We're using a ControlNet gateway to connect islands of automation.
All data to be passed is read by the controller that needs the data. There is no scheduled data going through the gateway. 25 PLCs communicate through the gateway at any time.
The gateway has the following configuration:
Slot 1: 1756-ENBT
Slot 2: 1756-CNB/E - Rev 11
Slot 3: 1756-CNB/E - Rev 11
Slot 4: 1756-CNB/E - Rev 11
Slot 5: 1756-CNB/E - Rev 11
Slot 6: 1756-CNB/E - Rev 11
Slot 7: 1756-CNB/E - Rev 11
All L62 and L63 PLC control net modules are 1756-CNB/E - Rev 11.
There are a few CompactLogix. The communications time-slice
is set to 40% for all PLCs.
The 1st DINT in all communications blocks is a constantly changing watchdog value. This value is monitored by the reading
PLC in order to see if communications hang up.
The problem is that communications occasionally stop for more than 10 seconds. By monitoring the watchdog we can see that
the data typically updates every 300-400 ms (worst case).
I'd appreciate any help that anyone could provide.
Thanks,
(8{)} :) .)
(Yosi)
I´m about to start a new project (Contrologix), I have to heat edible oil up to 235 degrees centigrade using a heat exchanger, due to production...
2,695
I am using a PID instruction to control system speed reference to two drives, based on the end of line machine current load. The requirements are...
6,345
The title sums up the control system setup. L63 processors with 1756-EN2T for Ethernet I/O which includes over 150 Control Techniques drives...
4,220
Dear Experts Is it possible two have following functionality using conrologix processors & I/Os at remote We have two separate redundant...
3,919
Can anyone confirm that using contrologix 5580 controller is not possible to work with powerflex 527? It's been a couple of days now that i am...
1,190