Contrologix PID output locks up
diat150
Mar 2006
Louisiana
1,475
Hello,
I have a flow control PID that keeps locking up. It seems to control fine but after a while the output no longer moves. For instance right now the cv is stuck at 84.85. right now I dont have the tuning parameters very aggressive because we are experimenting with running the valve in auto as opposed to manual, which is the way they have been running for years. I didnt write this program, just here helping out.
The process error is constantly changing, right now it is around .2% setpoint is currently 4 but if I drop to 3 then the cv starts moving again. Just wondering what could possibly be causing this. Maybe there is a setting that doesnt allow a change when the error is low?
There might be a deadband value entered. Is this PID or PIDE instruction? Can you post a screenshot of the configuration?
What does the 0.5 represent? Percentage? Engineering units? Raw value?
Can you do a trend on it? Capture the setpoint, process variable, error and control output. If everything is scaled into engineering or percentages, it's easier to understand.
HI ALL, I am trying to write a program with rslogix 5000 for contrologix is there any other ways to modulate a valve with out using PID blocks...
8,492
What is the safe max amount of pid loops that i can put into a contrologix processor without overloading it? These will all be steam valve...
3,356
What is the difference between the pid and pide instruction? Where and why would i use one as opposed to the other. My equipment has pid...
9,762
What is the best method of temperature controls single loop controlers or pid loops in a plc? What are the primary differences between the pid...
7,889
I am using a PID instruction to control system speed reference to two drives, based on the end of line machine current load. The requirements are...
6,362