I doing conversion from Panelview 1200 to Panelview Plus 1250.
I have open the project in PDS software. I couldn't understand tag addresses assign to the objects (eg. Numeric displays) It is something Like B 0 3 20/0 thru 20/15.
This panelview is communicating with PLC 5 PLC.
Can any one please help me with this.
Any have any document for programming Panelview 1200.
Thanks in Advance
HI,
B= block transfer data source type (vs assigned rack I/O type addressing)
O= block transfer type, O = write, I= read (PLC processors perspective)
3= block transfer number, three in this case, there could be several blocks. At least three in you case.
20= specific word of this block, don't forget, word zero is used.
/0 thru /15= the specific bits of word #20 that are used in this object. looks like a SLC word. PLC5 would be /0 thru/17 (Octal) if my memory is correct.
SO.. somewhere in the CPU there is a block transfer (write) that uses for instance say N10:0 thru N10:31 for a 32 word block that is written to the panel. The example object is word 20 so.. N10:19. I always get confused on the word number designation. Is word "N10:0" word #1 or is it word number zero? A quick look at the block transfers in the cpu should let you know what word this object is using. Write it down on a legal pad & keep a ledger of the addressed as they are discovered. You will soon be on your way to another project.
BD
HI,
BD
HI BD
Thanks for the reply.
Can you please explain (D I 07 3 2 Dig ) what this address means.
thanks
VB
D= Discrete I/O type (Rack assigned I/O)
I= Input from processors perspective
07= Rack #
3= Word#
2=Bit#
Search processor program for- I:073/2
BD
Hi all, I'm in the process of upgrading a PanelView1200 HMI program to be developed in FactroyTalk View Studio. The filetype for PanelView 1200...
292
I have a failing Panelview connected to a SLC 5/04 over DH-485 using a pair of SLC 500 Link couplers as the PLC and HMI are about 125 feet apart...
2,438
Currently have an old PV 600 hooked to the side port of a ML1500. Originally the driver in the Panelview was listed as - -Serial-DF1...
1,594
I have the opportunity to do a start-up this Monday-Wednesday. They needed someone who could download a revised file on a ControlLogix and PV...
2,676
I need to convert a PanelMate eProPS application to a PanelView Plus for a customer. I do not have the panelmate eProPS software but I do have the...
2,326