Conversion from PLC-3 to ControlLogix
khurley1001
Oct 2006
Ontario
I am converting from a PLC-3 to ControlLogix and our existing program uses Status bits (S0:2/13) to alarm a Rack Fault (RIO). I need to replicate this in the ControlLogix (using 1756-DHRIO to 1771 IO). Information on the AB website is as follows:
"There are no bits in a ControlLogix system that are the same as the fault bits in a PLC-5."
Does anyone have a good solution for this?
Thanks in advance.
Kevin:
Check out the RackStatus words created for each ASB module. There's lot's of rack status info there.
Jim
Jim,
The AB technote says:
"The RackStatus member of the input tag is a diagnostic tag for the whole adapter - 0 if the data is good, non-zero if the data is bad."
Currently I am using R23:I.RackStatus NEQ 0, but I was not sure if there were any scenarios where this would not provide an alarm.
K
Hi, I have converted PLC5 code to Controllogix. Having problem with PCE errors relating to Status File(S:4) and Indirect Addressing. In the...
3,044
Hi there, I have a request from one of my customers to do a PLC 5 to ControlLogix conversion. I familiar with the programs and the design. What...
4,055
I have a machine which is undergoing upgradation. As part of the process two SEW drives are being replaced., existing Gen B with new Gen C. The...
220
Hi guys, I have no experience when working with AllenBradley PLC, but I hope someone could clarify the result of multiplication shown in the...
2,216
Does anyone know where I might be able to download or obtain a copy of Allen Bradley 6200-2CV5 software to convert a PLC2/30 to PLC 5? I'd like to...
1,514