CP-342-5 communication
Ralphf
Aug 2011
TEXAS
Basically what I am looking to do is move some basic digital Inputs and outputs between 3 PLCs. The system is already setup and has
Station 1. - CPU-317, 342-5, 342-5, I/O modules
Station 2. - CPU-314, 342-5, I/O modules
Station 3. - CPU-315, 342-5, I/O modules
Stations are interconnected with 342-5 modules and by Fiber using OLMs
Communication profibus no DP
Station 1 has database tables
Send DB90
Receive from Station 2 DB92
Receive from Station 3 DB93
Station 2 and 3 both have same setup as far as tables go.
Send DB100
Receive DB101
They currently communicate and everything working fine right now...
What I want to add to what is existing is take say on Station 3 take I5.2 and have that output on Station 2 as Q7.2
I think what needs to happen is on Station 3 I add to FC to set
DB92.DBX14.5 = I5.2 (14.5=next unused value)
Then on Station 1 in FC set DB100.DBX14.4(next unused value) = DB93.DBX??.? (here is where I run into problem explain more below)
Then on Station 2 in FC set Q7.2 = DB101.DBX14.2 (next unused value)
My problem is I can't figure out how or where the program takes the DB table and sends/receives the data. I tried to follow some data from the existing code but it goes I5.0 -- DB100.DBX14.2 --- DB92.DBX6.2 -- then to logic...
It would make sense to me if DB100 was sent from Station 3 and on Station 1 that table was repeated in DB92 So DB100.4.1 was the same data as DB92.4.1 but that does seem to be the case. I can't even find where it says.. to load the incoming data in DB92 or send from DB100 etc... Maybe if I can find that I can see the offset or where it does assignments etc. Is this something I can only see on the online code? (Working with just the offline code right now)
Your help figuring this out would be much appreciated.
Ralph
by that, I take that you are not the original programmer.
The way you describe it, it sounds as if the data is tranferred via a configured NetPro connection and Send/Receive (because of the "no DP"). Look for the blocks AG_SEND and AG_RECV.
(the words "send" and "receive" are sometimes also used when the datatransfer is via Profibus master-slave, because the blocks DP_SEND and DP_RECV must be used in that case).
The source and destination configuration of the AG_SEND and AG_RECV blocks will reveal why there is an offset so that a bit is in byte 14 in one DB and in byte 6 in the other DB.
Apart from that, I think you should not touch the setup of the datatransfer. In stead, just map out at what adresses the inputs in one CPU arrive as data in the other CPU, and vice-versa. Then you will know what to do.
No I am not the original programmer. Problem is there isn't any send / receive blocks unless it is in a protected system call.
Will try just to use the empty space and see how it goes. Would really like to know where the info is for the data transfer though.
Is there somewhere that you could point me to that has examples of the dp_send receive blocks so I make sure I am looking for the right thing?
thanks for the help
Ralph
AG_SEND and AG_RECV are protected blocks, but they should still appear in the cross reference.
If you look at the blocks view in Simatic Manager, you can try to look for AG_SEND and AG_RECV, and for protected blocks (there is a small padlock symbol next to the block icon).
I want to configure s7314ifm plc with cp module cp342-5. And after that I have to communicate cp342-5 with a vfd through profibus dp cb15. I don't...
2,368
HI. AM JUST TRYING OUT TO RUN A MOTOR FORWARD AND REVERSE BUT WHERE DO I EVEN START....? PLEASE HELP... HARDWARE CONNECTIONS ARE OK BUT JUST CANT...
1,476
Dear All My client has Machine having S7-300 plc network as attached Node having address 5 marked in red is not communicating .machine is running...
26
6,490
We have changed a S5-95U/L2 with a S7-314C/CP342-5 and can not get the communication running.Using the standard FC5 an FC6 and can see that the...
2,289
Hello, I need to make a connection between an ET200S and a CPU313C through profibus, so i bought a CP342-5 module. I followed the manual from...
4,287