Creating a heartbeat tag in CompactLogix to keep track of communication
Rob S.
Sep 2008
Maryland
739
Good Evening ,
I have 2 CompactLogix PLC's , that I am going to use Produced / Consumed Tags . I would like to tell if both are communicating , and if not create a fault. How do you create a system or clock bit in a CompactLogix ? I remember in the SLC 500 , I thought , that you had S: bits that would do similar things .
Thanks in advance ,
Create a UDT to transfer back and forth. Make sure that the first element of the UDT is of data type "CONNECTION_STATUS". There are two BOOLs inside it that will be automatically updated. You can then put whatever else in the UDT that you would to transfer, such as a DINT array.
The posts above are how I do it too.
But, just to answer your original question, there are no "clock bits" on the Logix 5000 platform. I have an AOI that I import into all my projects to give me flashing bits, timing pulses and the like, should I need them.
Alternatively, if you don't like using UDTs, you can just create a DINT in each PLC called "Changing_Value" or whatever. Have each PLC increment their own value every scan. Monitor this value on the other PLC, and if the value doesn't change for x seconds, then you have lost the connection. That's the way to do it without the S bit from RSL500.
Yes, you can create/edit/delete UDT's online, as long as they're not being used. So if you create a UDT and then create a tag of that type, you can no longer edit the UDT online. If you need to change it, you either have to do it offline and download, or delete your tag, edit the UDT, and re-create the tag.
A little bit of messing about, but it'll get you there.
Connection status does indicate run mode.
I don't think you can create produced/consumed tags online. At least you couldn't in the past.
Does the connection status indicate connected if the PLC is not in run mode..?
If so, then a changing value is the best bet, IMO
Yes, the CONNECTION_STATUS gives you two bool's - ConnectionFaulted (which should be off for a healthy connection) and RunMode (which means the target PLC is in run mode, and should be on for a healthy connection).
Even if both PLC's are in program mode, these tags will still accurately reflect the state of the connection and the mode of the PLC.
In RSLogix 5000 Help file\Contents. under the INDEX Tab Type: New Tag dialog box overview
You can create base tags and alias tags while the controller is online or offline, as long as the new tag is verified. You can only create consumed tags while the controller is offline.
Choose this type if you want to make this tag available to remote controllers through controller-to-controller messaging. This parameter is unavailable when online; you must be offline to choose to produce a tag. This parameter is also unavailable for tags that cannot be used as producers
You will also find the setup information on new tags.
The idea here is to provide for a brief rapid influx of message codes while preventing sequentially repeating the same message. i.e. if two...
23
683
Hello everyone, In a factory where we installed Citect 7.20 the computer began to show the first signs of end of life. They never considered...
75
Hi everyone, I'm a last year student at the university in Ghent, and for my thesis i need to write a TwinCAT program that writes data to a .daq...
143
When I go to create a new module in Studio 5000 I can't enter any information for the IP Address or change any other fields. Is there any fix to...
255
Hello I am kind of new to the Rockwell world, i've mainly worked with Siemens and Schneider untill now. I am to make a HMI application running...
1,064