Hello, I am fairly new in the field and I am having trouble creating a set point for a pressure transmitter in Studio5000. My question is, how exactly do you write to the transmitter and tell it that you want a certain value to be maintained. I obviously will have a reading coming in from the device, I'm just not sure where I would send the command to change the set point. (I am using an IFM "PI2794" with IOlink.) Thanks in advance for the input.
I'm not an IO Link expert but I think you will find what you are looking for in here:
https://www.ifm.com/download/files/_ifm-000100-20140130-IODD101-en/$file/_ifm-000100-20140130-IODD101-en.pdf
It looks like the value you are looking for is at index 70. I'm not sure how you trigger that data down to the sensor.
Keith
a set point for a pressure transmitter, <snip? a certain value to be maintained.
The device is transmitter with an alarm output. The switching alarm output could conceivably used as a stand-alone on-off controller driving a solenoid valve to achieve a pressure value within the plus/minus hysteresis of an on-off control loop.
What are you using the 4-20mA pressure signal for?
The transmitter only gives you a pressure reading. You can not control the pressure with the transmitter. You need the valve of the pressure and make a logic in your plc to open/close valve to cause a change in the pressure.
Are talking about the setpoint for an alarm output
The idea here is to provide for a brief rapid influx of message codes while preventing sequentially repeating the same message. i.e. if two...
23
678
Hello everyone, In a factory where we installed Citect 7.20 the computer began to show the first signs of end of life. They never considered...
74
Hi everyone, I'm a last year student at the university in Ghent, and for my thesis i need to write a TwinCAT program that writes data to a .daq...
141
When I go to create a new module in Studio 5000 I can't enter any information for the IP Address or change any other fields. Is there any fix to...
253
Hello I am kind of new to the Rockwell world, i've mainly worked with Siemens and Schneider untill now. I am to make a HMI application running...
1,064