CTI 2500-200 running PID
Ted
Sep 2007
Kansas
Hello,
I am using a CTI 2500-200 plc and 505 WorkShop and can not get PID loop to do anything. The program is stripped down to 1 rung and the PID. In the PID it is Enabled, the
PV Addr = V1
Loop Output Addr = V2
Remote SP = V3
I modify V1 and V3 to get the output to move, but it does not.
Am I missing something simple ??
Thank you
Ted
What are your V-Flag addresses? You have to to place the loop in auto and give it a setpoint. The remote setpoint only applies when the loop in in cascade.
You can manipulate the loop via a SFPGM or by setting bits in the the V-flag word.
To assign a setpoint use this in a SFPGM, I assume you are using loop 1.
MATH LSP1 := 50
Here's a chart on the v-flags:
Bits 4 & 5 will give you the loops current mode, you can place in cascade by energizing bit 3.
Just a friendly reminder, the bits in words are somewhat different than most PLC's.
The MSB is bit 1 and the LSB is bit 16.
While most often MSB is bit 15 and LSB is bit 0.
505/2500
1,2,3,4,.......16
AB/others
15,14,13,12 ...........0
Hi All, Long time since my last visit. I have a problem with my TI/Siemens505/CTI PLC. I need to configure new IO in the existing Profibus IO...
2,118
Hi There, I have a problem with my CTI 2500-C200 CPU; It is anew release with Firmware 6.02 and CPLD 6.02. My CPU is getting a Fatal Error with...
2,885
Hi I am trying to find a suitable OPC server for the above plc. I will be using the ethernet port on the processor and not via the sperate 2572...
2,775
I'm having trouble programming a PID loop in 505 workshop. Are there any examples out there of how to program this, or how it even works? I got a...
1,493
Can a Siemens TP277 communicate with a CTI2500 CPU via the ethernet port? There are only DP and serial selections for the Simatic 505 in the WinCC...
2,145