Customer wants to buy a back-up SLC 5/05...

AutomationTechBrian

Lifetime Supporting Member
Join Date
Jul 2013
Location
St. Cloud, MN
Posts
669
We have been talking about upgrading a customer's machine PLC and HMI... It might happen sometime next Fall. That said, about a month ago, his SLC 5/05 crashed, and I installed his back-up CPU. Now, the customer has asked us to find him a back-up CPU in case this one fails before the upgrade. I remember reading info on this board about being careful about buying SLCs on Ebay. I can't find the discussion, and I need to pass some guidance to to our buyer. He typically avoids anything being sold from China, but I remember hearing the problem extends beyond that advice. Here is a picture of the current CPU. Is there any specific info I should give to him about sourcing a 1747-L552?
 

Attachments

  • 1747-L552-SerB.png
    1747-L552-SerB.png
    194.2 KB · Views: 4
Most reliable (and most expensive) would be to buy a new one. They're at end of life to be discontinued 3/31/2024 with a list price of almost $16k.
I would probably refer them to a place like Radwell that's US based and has a warranty. And then test it immediately upon receipt.
 
If it's a critical spare, I would buy from a refurbisher like www.radwell.com. warranties, certified, and you know it's genuine. You'll pay more, but the customer will have peace of mind.

There are also a couple of members here that sell used parts, so you might try them as well.
 

Similar Topics

Hi. We have several automation systems on a plant which runs on different PLC’s. We also have a topside network system that shows all the...
Replies
8
Views
746
I have 10 years expereience about programming TwinCAT2 PLC. However, there is still one thing that I can't find a best solution about updating the...
Replies
0
Views
800
Good Evening , I have a customer that purchased a number of Omron G9SE-201 safety relays. Does anyone have a detailed manual or training...
Replies
2
Views
3,685
My customer's customer base is growing exponentially. He needs to electronically assign a new case # to tech support calls. And it has to be...
Replies
2
Views
911
Hi all, S7-1200/1500. One of our customers wants to have a notification on the HMI that a connection is live via the remote maintenance modem...
Replies
6
Views
1,748
Back
Top Bottom