Delta plc real time clock
splendid8877
Aug 2013
Penang
25
Hi all,
I'm planning to set a timer that everyday each 1 hour to on pump.
And If the power trip and then to on back the PLC, the plc still continue to counting.
For example:
I)7pm pump on
II)after 1 hour is 8pm pump on again
III)during 8.35pm power trip
IV)soon after 8.40pm power on back PLC
V)then 9pm pump on neither 9.05pm or 9.40pm pump on
Is it possible to write this program in delta PLC?
Thanks in advance,
Ct
http://www.delta.com.tw/product/em/control/plc/download/manual/DVP-ES2_SS2_SA2_SX2-Program_O_EN_20110302.pdf
Yes this is possible.
You may want to start a memory retentive timer for the pump when it is turned on. This way when power is restored (First Scan Bit) it can continue for the time duration.
Regards,
During the PLC power off, is it the PLC still capable to continue counting?
I would like to set the timer is accuracy even the power off delay 10 minute but still on time to on pump.
For example:
I)7pm pump on
III)during 8.30pm power trip
V)then 9pm pump on neither delay until 9.10pm or 9.40pm pump on
Best regards,
Ct
The PLC scan will stop if power is removed from the PLC. The PLC will not continue to count.
The real time clock (RTC) is battery backed and has the accuracy of approximately 120 seconds per year. You will have to check the model you are using for exact numbers.
Storing the RTC in internal registers every scan will allow you to know the exact time of the last known scan. Using the first scan bit will allow you to compare the RTC and make the required modifications to the timer for the pump.
Regards,
Dear all I need help for delta plc programming . I can use DVP-12SE PLC and HMI DOP-B10E615 as they both support ethernet. I am planning to make...
1,515
Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
44
I'm trying to write a data in Arduino using MODWR function block .I used the code I got from online for both PLC and Arduino. I made the wiring...
119
I have downloaded COMMGR 1.15 software on my laptop. After downloading it works. When I stop and start the program again it doesn't work. It is...
154
How i Can connect Delta plc, with Beckoff remote IO cards?
178