Hi All,
I need to dispaly an alarm whenever communication link between Simatic multipanel HMI and GE90-30 PLC is failed. There is a system event "Connection to PLC interuppted" in the WinCC Flexible which will be displayed when communication is failed but will be dispalyed for few second only on alarm page. This event does not required acknowledgement and will disappear from alarm screen in few seconds.
I need to configure an alarm for "Communication Failure" such that it remains on the screen until somebody acknowledges it.
All the helps and advice are appreciated.
snippet from Siemens
It sounds like you want the MP377 to know it has lost the connection to the PLC.
In case you wanted the PLC to know it has lost the connection to the MP377 there is an area pointer for this. You set it up on the Connections - Area Pointer tab. It is called "Coordination" and the 3rd bit is the Life bit: inverted by the HMI device at intervals of approximately one second.
http://www.automation.siemens.com/WW/forum/guests/PostShow.aspx?PostID=60035&60035&Language=en
This solution worked great for me
Does anyone know of a way to detect if someone is online with the controller in ControlLogix (from logic) I'm thinking that maybe there is a CIP...
391
Hi all, I am trying to find a way of detecting a motor is not isolated before attempting to run an inverter. We would normally use a 4 pole...
19
3,082
Hello everybody, I have a vendor system that has some remote monitoring (read only) and remote control (read/write) data that is available via...
2,876
1,221
Hello.We are using S7-300 Cpu.Sometimes give an error.OB86 and OB122 blocks called.OB86 Block ; L #OB86_FLT_ID T...
1,932