DeviceNet config problem
Geza Kelemen
Apr 2002
17
Hello,
It is possible to configure Flex I/O ( 1794 series ) by Passthru Ethernet to DeviceNet.
I got this error list . What I made wrong. Any idias?
And doesnt the 1747-SDN have to be above a certain firmware to allow passthrough ?
4.xxx summin springs to mind but i cant be sure without looking it up ?
I can upload the module information from Flex I/O adapter virtual chassis,
when I try to download ( to save the modules setting ) I got the error list.
In my opinion the SDNPT driver is OK. I don't have problem configuring
the ARMOR blocks and download to the scanner ( 1792D series )
Those error codes are unusual, but one is very common when dealing with 1794-ADN adapters; the "object state conflict". Likely the other stuff involving proxies is consequential to the passthrough mechanism.
When a 1794-ADN has an I/O Connection established, you cannot re-download a new configuration into it. This is true even if the I/O connection is in a faulted or incorrect size (Error 77) state.
So, the standard procedure for re-configuring 1794-ADN adapters is to remove them from the 1747-SDN scanlist and cycle power to the 1794-ADN adapter. That allows the adapter to reboot and not establish an I/O connection, which makes it receptive to reconfiguration.
Ken,
We talked with out A-B contact person, and he told us, the communication band for SLC 505 is not wide enough
to use passthru for configure Flex I/O. Passthru is valid just for ControlLogix.
We need to use the 1770-KFD, RS232 to DeviceNet module for this job.
What is your opinion?
Thank you Ken,
What I did wrong :
"" So, the standard procedure for re-configuring 1794-ADN adapters is to remove them from the 1747-SDN scanlist and cycle power to the 1794-ADN adapter. That allows the adapter to reboot and not establish an I/O connection, which makes it receptive to reconfiguration. ""
Need some clarification regarding the devicenet set up PLC is CLX with 1756-DNB scanner, trunkline using kwiklink flat cable with the micro...
5,167
Looking for help in configuring explicit messaging in the RSLogix 5000 for devicenet 1336 drive is 16bit and current devicenet is mapped this...
3,217
Hi, The point io AO card OE2C will not take any output value. It also resets its configuration (edited in RSNetworkx for DeviceNet) every time...
3,217
I am attempting to configure a Devicent 1747-SDN offline to communicate with a SquareD MCC. The MCC is using TSX Momentum 170 ADM 540 80 6point in...
3,673
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...