Devicenet remote I/O

No.


Briefly:
  1. Make sure you don't assign a duplicate address.
  2. Add the module to the scan list and download to the scanner module. Use RSNetworx for Devicenet for this.
  3. Configure the added module's input and output datatable addresses. The size of these parameters can vary depending on the type of module.
There are other settings but these are the basics.

Others with more detailed info will be along.
 
In general, you need the software tools in order to configure a new device on the network or alter an existing device (like the Scanner).

There are a handful of exceptions, like systems built with QuickConnect and the auto-Scanlist feature.

If you're using Rockwell Automation controllers, the software tool is RSNetworx for DeviceNet. If you're using Omron or DeltaV or some other controller, you use their tools.
 

Similar Topics

Hi Guys, I am still fairly new to RS Logix so please bare with me. I have been asked by a client to add an additional IO card at one of their...
Replies
11
Views
12,140
Hello I have a customer with a bad and very long serial network that would like to upgrade thru ethernet. I was looking to install 2 gateway...
Replies
4
Views
4,226
RSLogix5000 forcing real I/Os, through a devicenet protocol, in a remote rack where all I/Os were terminated, also being new in this PLC...
Replies
8
Views
3,480
Hi. We've been asked to do an upgrade on plant, consisting on a PLC upgrade. This involves replacing a 1747-SDN module to a 1769-SDN, in a network...
Replies
0
Views
41
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
132
Back
Top Bottom