Dh-485 Network Question
mattbdb
Feb 2003
I am trying to link 3 pieces of assembly equipment to one PC to make it easier for the maintenance technicians to troubleshoot a problem rather than connecting to indvidual robots using a PIC driver. I am using one "1" PC and using three "3" SLC 500 DH-485 LINK COUPLERS to do this. I believe I need to "daisy chain" link these together but I don't know where to start. I need information on what cables and other things I would need to set this up. I would just buy a module for this but I am trying to save money and use what I already have . Any information about DH-485 and specifcally concerning my issue would be greatly appreciated.
You are off to a good start. Each SLC-500 controller is going to need one of those 1747-AIC "isolated link couplers" to connect it to the DH-485 trunkline.
Belden #9842 is a good multiconductor cable to use for DH-485 trunklines. That's the cable with which you will make the "daisy chain" connections between the AIC couplers. Publication 1770-6.2.2 is the authoritative reference on this cabling.
The 1747-AIC couplers connect to the SLC's DH-485 port with a cable called a 1747-C11. They have an unusual "AMP" connector on one side and it's impractical to make them yourself.
On the PC side, you might have a problem using a 1747-PIC or a 1761-NET-AIC with the "PIC driver" in RSLinx. It's been discussed at length both here and elsewhere that many PC serial ports today don't supply the necessary RS-232 voltages to run those devices. If you have trouble with your existing hardware, a 1747-UIC USB/DH485 interface will be the inexpensive option to connect your PC to this DH485 network.
I have an application running an AB micrologix 1200 and a DH485 Panelview 1000. They are connected through a Net AIC module. Now my boss wants to...
4,465
Good day all. I have an RS-485 topology question. I am hoping for some guidance so that I can make a confident calculation/decision that this will...
1,508
I have an allen Bradley system in which there is two micrologix 1200 and two panel view 300 and a Rsview 32 connected on DH485 network with the...
1,776
Hi, i am trying to create an DH485 netwrok which will consist of 2 ML1500 using ACi units for data acquisition back to a pc. i understand how...
2,009
Hi, I am stuck with RS485 network with duplicate node. I changed address of a node by mistake and now cannot talk to any node possibly due to...
5,571