Hello Friends
I need to communicate a 5/04 with a Micrologix 1400 to send and receive some bits and integers, also I need to connect ML1400 to MatrikonOPC.
In the 5/04 the Channel 1 with DH+ is free.
The Channel 0 with DH485 is connected to a Panelview just with DH485 port.
The 5/04 also has a 1747-SDN devicenet Scanner. I had thought in a 1761-NET-DNI but this module has been discontinued.
Also I had though in a 1761-NET-ENI, but this module does not support DH485, just DF1, and this module will be discontinued.
Change to 5/05 CPU is to expensive.
Is there a DH485 to Ethernet Interface?
Or another way to connect the 5/04 to ML1400?
Thanks in advance. :)
MicroLogix 1400 Protocol Support:
Channel 0:
Series A: DF1 Full Duplex, DF1 Half Duplex Master or Slave, DH-485, Modbus RTU Master or Slave, ASCII Read/Write, DF1 Radio Modem, DNP3
Series B: Same as Series A
Channel 1:
Series A: Ethernet/IP (Messaging/Explicit,) BOOTP Client, DHCP Client, SNMP Server and Client, HTTP Server, duplicate IP address detection
Series B: Ethernet/IP (Messaging/Explicit,) BOOTP Client, DHCP Client, SNMP Server and Client, HTTP Server, duplicate IP address detection, Modbus TCP, DNP3 over IP.
Channel 2:
What's the panelview reference?
If it can support DH+ you can switch to CH1 and use CH0 to communicate DF1with ML1400.
Also if your panelview support DF1 you can use CH2 of M1400
Hi asteroide,
Please note that I am by no means an expert in RockWell equipment...
Still, I would suggest an Anybus X-gateway, that will act as DeviceNet adapter on one side and Modbus TCP slave on the other, such as:http://www.anybus.com/support/support.asp?PID=245&ProdType=Anybus X-gateway
My understanding is that the ML1400 supports Modbus TCP nativly.
Also, included with the gateway you will get the Anybus OPC server... :)
My 2 cents
Patrick L
Hello
The Panelview is a 2711-B5A5, this has just 1 port : DH485.
SO, I need a port splitter (1747-DPS2) to connect the panelview and a interface DH485 to Ethernet.
Maybe Lantronix UDS1100 could be used? Supports RS232, RS422 and RS485 communications. The port in the 5/04 is DH485, RS485 is the same or not? :S
Also I looking for a Devicenet to ML1400 (1761-NET-DNI has been discontinued).
From Anybus I think this Devicenet Gateway could be useful: RS232, RS422, RS485
http://www.anybus.com/products/products.asp?PID=105&ProductType=Anybus Communicator
Thanks for your help:)
DH485 and RS485 are not the same and using a port splitter on the DF1 port will only work if the DF1 port is set to DF1 Half Duplex master. Because it (the DF1 port) is connected to a PanelView it is more than likely setup as a DF1 Full duplex port. You could change that but it’s going to involve re-configuring the both the SLC and the PV. You could use a DeviceNet to EtherNet/IP bridge but it’s going to get complicated and cumbersome. I’d explore replacing the SLC5/04 with a SLC5/05. That would give you an Ethernet port and a lot more flexibility with regards to accessing the SLC. With the SLC5/04 in order to get online with it you have to disable one of the functions (I.E. take the DH485 connection off line or the DF1 connection off line). With Ethernet you don’t have to break the connection to access it.
Hi asteroide,
Sure, the Anybus Communicator for DeviceNet should also work. Do note that it can only act as Modbus RTU master and thus the ML1400 has to be set up as Modbus RTU slave.
BR
Patrick Lansdorf
I've got a DeviceNet card (1756-DNB) in a Logix 5555. Can I transfer I/O info through an old SLC 5/03 on it's DH485 RJ45 jack? Or somehow through...
1,601
Hello all, i have seen a few things here and there about connecting to a panelview 550, however i still would like to ask a few things, I have...
140
Hi all, I had a setup with 2 Micrologix 1100 connected to a Panelview C300 over DH-485. I was mandated to upgrade the HMI, and proposed to...
903
Hello, We have an older machine that has a standard PanelView (2711-T10C3) connected over DH485 to a SLC 5/04 PLC via a 1761-NET-AIC module in...
684
Hi, I have a SLC5/03 connected to a working HMI via RE232 port, and connected to a broken HMI via DH485 (RJ45), I want to use the cable that used...
3,327