DLR and SCADA with Compactlogix
smiller
Aug 2003
Arizona/Brazil
116
I am looking into implementing Ethernet I/O on an upcoming project. My question is: What is the best method to have Ethernet I/O AND a separate network for the SCADA system with a Compactlogix PLC? Since the Compactlogix only allows a single subnet network connection I am unsure how to get connectivity to both separate networks with a Compactlogix. does anyone have experience with this type setup?
A few years ago we did what you described. We use an L45 with 2 1768-ENTBs (I think that the part number). Just remember you have to mount the Ethernet modules to the Left of the controller.
This allowed remote IO on one network and the SCADA for other.
You will need the 1783-NATR device. This will break out a port on your DLR network for a SCADA port, and it will allow you to use NAT to map your PLC IP address (say 192.168.1.10) to the SCADA network IP address say (10.10.1.10).
Previous posts apply to the older CompactLogix controllers.
http://literature.rockwellautomation.com/idc/groups/literature/documents/pp/enet-pp011_-en-p.pdf
Thanks Paully. The NATR looks like what I need. I wanted to avoid the 1768 controllers since they are not being supported in the newer versions of Logix.
:geek: Good knowledge right there. Any specific reason the example architecture on the pamphlet shows two NAT modules? Or than to show they can be piggybacked?
It is showing two machines that have identical IP addresses. Its showing that you can have completely duplicate machines, IP addresses included, and use the 1783-NATR device to make them unique to the plant network. This means an OEM can supply whatever network configuration they want. In the past the OEM would have to be assigned IP addresses from the plant.
The 'other' device that is connecting to the DLR network to the LOCAL HMI, well that is not a 1783-NATR, that is a 1783-ETAP. The ETAP doesn't do NAT, it's simply there to breakout the DLR network to a non-DLR device like an HMI. Or to extend the network to a non-DLR section of that local network, perhaps a switch.
Hello all. I need some help on DLR issue we encountered which is the DLR not working when supervisor is disconnected from the ring. FIrst of all...
145
Greetings Folks, This is my first post after a long gap (almost 13 years) on this forum and i hope that i will get things fixed with your...
291
Hello, I have a small DLR ring set up in a lab that consists of 1 Stratix 5200 and 2 ENTR/Cs. I am having an issues only on recovery of the ring...
167
Hello, I have been trying to figure out how to connect to and monitor a DLR that is on a remote rack from my PLC. The local has a 1756-L81E and...
124
HI I have a stratix 5700 switch 1783-BMS10CGA and I am asking if I can configure it to do a ring topology. So what can I do to configure it. I...
474