Hello.
This one is as nerdy as it can get. Never seen this issue before.
I am seeing a "Partial Network Fault", for which the specification only says: Vol 2, Clause 5-6.3.4 Network Status Values:
"A network fault has been detected in one direction only. Valid only when Network Topology is Ring and the node is the active ring supervisor"
The catch is, I am not using a normal DLR, but the DLR as specified in the ODVA test specification for DRL node. This environment used to work but now I see this very strange behaviour.
I have tried to show what I have in the screenshot below.
Interestingly, if instead of switch B I use and unmanaged Ethernet tap the ring goes to normal status.
In this strange partial network fault condition, the activity LED in the port of the next node in the ring, connected to the L13ER supervisor is flashing, but the LED in the L13ER itself is off!
As you can see in the screenshots there is traffic on both switches, so I do not understand why the activity LED in the L13ER is not flashing. Really interesting,
I am intrigued about what can be the reason for this strange situation.
I am using LAN cables with only four lines between the DLR devices and the managed switches, so all ports in the managed switches including from the managed switches to the PC go online at 100 MBps Full duplex, so I am ruling out PHY issues.
Anyway, thanks for reading to this point.

2023-01-12_PartialNetworkFault.jpg
 
This is above my network knowledge. I thought DLR is proprietary to AB so one can't use a switch, even a managed one to act as a DLR node.
 
DLR is part of the specifcation. There are other makers such as Phonenix Contact which support DLR node and supervisor.
That is a special setup dfor the conformance test of DLR devices. It is not used in actual machines.
 
Let me start saying that I know nothing about conformance test.
As far as I know, only DLR enabled devices can be part of the network and switched must have DLR ports (like Stratix) to participate.
Partial network fault related to the beacon been passed one direction only. I guess your non-DLR switches don’t pass it correctly.
You probably need to contact ODVA conformance people for help.
 
Hello Contr_Conn:
Thanks very much for your comments.
You may not know about the DLR conformance test, but you know more device-level ring technology than anybody I know, and have been so helpful to me in the past with my questions.
You are right. I have analyzed the data in more detail. It seems the switch A is not passing the beacon from the DUT. As you can see below, the trace in switch B shows the beacon pairs, while the trace on switch A shows only one beacon. With this understanding, I can think a bit more about it before I ask ODVA. This think used to work so I think I should be able to fix this.
Again, thanks for sharing your knowledge.
The purpose of my question was to understand the meaning of "partial network fault" in the DLR context. This I have achieved thanks yo your explanation.

2023-01-13_DLR_issue.png
 
Contr_Conn and JeremyM:
Thanks a lot for the follow-up and interest.
I got the system to work as expected. The screenshot below shows what normal DLR beacon packets look like.

I think the ODVA could spend a bit more time explaining what the required settings for the managed switches should be. It is not trivial.
Again, thanks very much to Contr_Conn for sending me through the right path.

2023-01-12_PartialNetworkSolved.png
 
My only ask, is not to use monster screenshots like these.
Almost impossible to see on the cell phone or iPad screen.
 

Similar Topics

Hello all. I need some help on DLR issue we encountered which is the DLR not working when supervisor is disconnected from the ring. FIrst of all...
Replies
4
Views
146
Greetings Folks, This is my first post after a long gap (almost 13 years) on this forum and i hope that i will get things fixed with your...
Replies
10
Views
296
Hello, I have a small DLR ring set up in a lab that consists of 1 Stratix 5200 and 2 ENTR/Cs. I am having an issues only on recovery of the ring...
Replies
0
Views
170
Hello, I have been trying to figure out how to connect to and monitor a DLR that is on a remote rack from my PLC. The local has a 1756-L81E and...
Replies
0
Views
127
HI I have a stratix 5700 switch 1783-BMS10CGA and I am asking if I can configure it to do a ring topology. So what can I do to configure it. I...
Replies
9
Views
477
Back
Top Bottom