Down Load to Micrologics

dsprules

Member
Join Date
Nov 2005
Location
essex
Posts
8
Trying to download to micrologics, download box thinks its an SLC and asking to change the key to program mode!
Any Idea's please!
 
Micrologix 1500 RS logix software 6.10.10

Trying to download pop-up box shows "SLC is in run mode, switch on processor to program mode.
 
Micrologix 1500 RS logix software 6.10.10

Trying to download pop-up box shows "SLC is in run mode, switch on processor to program mode.
 
A Micro 1500 has a switch behind the left door for run/rem/prog. Your switch is most likely in the RUN position. Switch it to REM for remote control of operating mode.
 