Encoder Pulses to Distance & Speed
whussain6
Oct 2013
Newcastle
108
Hi, I am sure it must be simple but my head is not working at the time.
I have
- Encoder pulses (Input)
- Pulse per Rev of the belt
- Belt circumference (mm)
mm_per_rev = (Belt circumference/PPR)
I am calculating distance d (m) = (Pulses) x mm_per_rev/1000
Question is how to calculate the speed?
I must have all this within AOI so cannot use time based routine to calculate the speed. But ms pulse is provided for AOI.
it must be something like
d2 - d2 / t2 - t1
what about rollovers etc.
Appreciate your help.
Speed = [distance traveled during last elapsed time] / [elapsed time]. If you calculate for example velocity every 5 seconds, then the velocity in m/s will be just the traveled distance divided by 5.
Rollover : if the total distance is for example >= 100000 then subtract 100000, then the traveled distance will be negative and to correct it just add 100000
Convert Speed units per scan speed to per second
Actually I am looking to convert speed units per scan which I am obtaining from differential distance to speed (m/s).šŸ™ƒ
To obtain a stable speed reading you need a precise time base, and the scan time of a PLC is not usually stable.
In addition you need to count an appreciable amount of pulses between measurements, I think there should be at least 50 pulses
If you put your speed calc code in a Periodic Task the scan time base will be precise. We do it all the time.
Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
18
1,044
Hi; We have 5ppr 12vdc encoders (06nos) available in stock which I want to use at a machine to upgrade it. But Fatek PLC, which I want to use...
1,620
Hi Everyone! i'm a newbie to PLC And i have a question, How do i count pulses from a encoder giving positional feedback? my plan is to use this...
1,722
Hello everyone! I have strange problem. I have plc, inverter (mitsubishi), incremental encoder (sick) and motor. When i set the frequency on the...
3,969
Hello. So we have a machine with a carriage run by a VFD driven motor. I have noticed that for some reason it periodically loses 720 pulses and...
2,924