ET200 SP HA DI card wiring with pulse input
Lc1
Jan 2014
Uk
59
Hello,
We have the following DI card that can accept 1,2 and 3 wire DI's
( 6DL1131-6BH00-0PH1). We plan on installing this card for use with a pulse output from a E&H flowmeter. From the manual it says that connections should be made to terminals:
can this be wired in the following way
a wire from uv0 ( +) on the card to + on the switch
a wire from DI.0 on the card to - on the switch
Am i correct that this card can be wired this way or is there something i am not getting
Deja vu.
And that's not my understanding of the wiring diagram and the terminal list.
The UVn and DIn how together, basically each input has its own sensor supply which allows for diagnostics. The negative is common for all.
Sorry yes, that's correct. I thought it was similar switch to the one posted yesterday which was three wire sensor.
You will need to watch for current leakage though, check the ratings for both. Baiscally the sensor is drawing current from the PLC input and you want to make sure that the current required to power up the sensor does not exceed the turn on threshold of the input.
Thanks. I’m second guessing myself with this type of card for some reason.
Cheers
Hello, We have the following siemens DI Card 6DL1131-6BL00-OPH1 ( 32 channel) my question is in relation to the wiring of this card with the V50...
887
Hi, I have a question regarding the DI module 6DL1131-6BL00-0pH1, i am confusing myself with the family of IO, this is a 32 channel module. Can...
989
Hello, We have the following DI card that can accept 1,2 and 3 wire DI's ( 6DL1131-6BH00-0PH1). We plan on installing this card for use with...
1,909
Hi all, is it safe to remove AI / AO / DI / DO card from ET200x (S) while its powered, I would like to see which OB events occur in such...
2,293
Hi I have a task to change a controlsystem on a plant. The existing PLC is a Siemens IM 151-8 with a profibus mastercard 6ES7-138-4HA00. My plan...
631