Trying to send a byte to a remote host via TCP.
Creating socket - success. supply instance to Open, Write, and Delete messages.
Open socket - success. (destination is being seen)
Write Socket - Error code 16#0009
Delete socket - success.
I've attached screen caps. I'm hoping I'm not chasing one of those pesky show stoppers that seem to get left out of AB documentation a little too often. Any suggestions on the error source?
Thanks in advance.
You've probably seen the list of Socket Services error codes in Knowledgebase Article 34290 (TechConnect required). Error 16#0009 reads:
Invalid socket descriptor. To resolve this error, do the following:
• Make sure a valid socket instance exists.
• Make sure the message source data format and source values are
correct.
• For CREATE message make sure Type and Family is set correctly
• For UDP Read/Write - make sure that Source tag member Family is set to "2"
I'm not an expert on the Socket Services, but I think that the Socket Instance number gets reported when you create the socket. Is that the 15432 that you see in the C/I/A fields for the MSG ? Does it change each time you create a Socket ?
Is 0 the appropriate Port Number in this case, so that it's zero along with the Address, for a local IP ?
Take a step back and verify that you're trying to do an ordinary TCP connection, and describe the target device and port.
the socket instance number is behaving as expected. i copy it from the create socket message results to the instances of the open, write, and delete as soon as it's available.
i put the address/port as used in the open message parameters in the write parameters and it did not change the results.
i am trying to perform a tcp client transaction. we have a wifi equipped target device i'm trying to write a single byte to by directing it to an ip/port. the other instructions all seem to be behaving as expected. the open fails if the device doesn't respond, so it seems to me the issue is entirely in the EWeb world.
i didn't have that list of faults, so thanks a ton for that.
You would save a lot of time by using the code from the knowledgebase.
It takes care of stupid mistakes like this.
followup
After getting the dumb mistakes sorted out, the EWEB code is doing pretty well sending tcp commands. Pandora's box has likely just opened.
Hi; In a cabinet of a machine, a Fatek PLC with an Ethernet communication card is working. In the same cabinet, there is a 1 kW inverter. When...
505
Hi all, I have a project which utilizes an L-33ER CompactLogix (v32), which will communicate with a RIO rack with a 1769-AENTR card in its Slot...
790
Does anyone here on the forums have any experience with Solexy I.S. ethernet isolators? The model we are using is BXF3S010N0018. Issue we're...
1,827
I want to be able to use a 3rd party device to read the IO modules from an SLC505 without the use of the CPU. All the communications modules i...
32
15,269
we have a 525 drive with a 25-comm-f2p module. that was giving us 4 solid red light for communication. replaced module now we get port light is...
1,345