L-33ER Comm Fail Routine to Ethernet Card?
slick_william
Apr 2020
Oregon
39
Hi all,
I have a project which utilizes an L-33ER CompactLogix (v32), which will communicate with a RIO rack with a 1769-AENTR card in its Slot 0.
The rest of the RIO rack is populated with I/O cards of various types (DI, DO, etc).
I am wondering if there is a way to generate a comm fail alarm if comms should be lost between the CompactLogix and the 1769-AENTR in the RIO rack.
Any help would be appreciated, thanks
(y)
Use a GSV instruction on the module. You can retrieve different module status' and generate the alarm or fault conditions you require.
@Slick_william:
I got a subroutine to test almost anything, it generates alarms if something is wrong.
Send me a PM with your email and it´ll be yours.
It works with Compact and Controllogix.
I got it in V20 and V32.
Hey guys, On my system, i got prop valve controling cylinder on the left and right to adjust the center of a lumber before it get in a woodmill...
933
Hi Friends, I have an upcoming project were I need 20 pcs of ModBus TCP Clients / AOI. to control 10 devices I use 20 transactions to control 10...
744
We have a machine that has a 1769-L33ER and we were wanting to connect it to our plant network. Currently has a local network for drives and HMI...
855
So, here's the situation the best I can explain it. I have a 1769-L33Er that uses a set of recipes selected by the customer via FT SE on a...
1,652
I'm trying to get an upload from a machine for backup purposes. The upload seems to work fine but at the end I get errors and no upload. It...
1,398