Greetings,..
Has anybody worked with Eurotherm 2408i digital indicator before?
i have to use them as Milk volume indicators in our 90 kl silos.(items delivered without wiring diagrams).
I have downloaded the diagrams from the net, but have few queries..
There is 24 vdc two wire ( 4-20ma) pressure transmitter at the bottom of the silo which has to be hooked on to the indicator to have digital readout in litres.
Should i have to use a separate power supply for the transmitter, ( i dont see any 24vdc supply available on the 2408i)
What specific parameters have to be programmed in the Prog menu to enable conversion of mA signal to volume of milk?
Any thoughts?
Cheers.