Ever need to put 120 VAC into a 24VDC Input?

Bob A.

Lifetime Supporting Member
Join Date
Jan 2008
Location
New Cumberland, WV
Posts
179
Just wondering if anyone ever came up with a simple and effective way to do the conversion? If so, I'm curious about what worked over time.

Bob A
 
Step down transormer and rectifier?

Otherwise I am curious to see if you have better luck - every time I did 120 into 24 I got this smoky stuff. Let me know what I did wrong.

Dan Bentler
 
Interposing relay.


Pretty much this covers any voltage miss matches. You can even do the same thing for outputs.

Just remeber the 3 gotcha's on using solid state relays.

1) You may need a pull down resister
2) Polarity matters on both sides of the relay.
3) If you short them to ground the relay generally stays shorted not open. Mainly happens on AC Solid State Relays
 
I'm assuming that you are powering a PLC 24VDC input. If the application can stand a short power-up delay, you could use a small cheapo 24VDC power supply of the wall-wart variety and just switch it on or off.
 
I'm assuming that you are powering a PLC 24VDC input. If the application can stand a short power-up delay, you could use a small cheapo 24VDC power supply of the wall-wart variety and just switch it on or off.

Yeah, I want my PLC inputs and processes relying on a cheapo wall-wart (n):D:D
 
Lots of replies here, but we also go almost exclusively with the AB DIN-Mount devices listed by Kid above.
We also use them for outputs that have to drive inductive field devices (like solenoids) or large contactors, etc.

A nice feature, is that the small relay module (or SSR Isolator if you choose) is replaceable from the top, without removing the whole base or un-wiring anything.
 
Transtronics has a range of opto-isolators fro various voltage conversions eg 24/24 24/120/ 120/24. Right now I am grappling with he 120vac to 24vdc version which unfortunately has a half-rectified DC output which must be smoothed.
 

Similar Topics

Hi everyone! First time posting to this, so should give you a bit of background info on myself to explain the situation i'm in. I am a beginner...
Replies
4
Views
1,576
Hi. Almost every time when working with PT100 probes the customers ask me "have the probes been calibrated?" The reason for the customers to ask...
Replies
18
Views
5,082
I am using Mitsubishi PLC :FX3g and downloaded the program in it. When I connect Mitsubihi FX2N-4DA expansion module, it lost its communication...
Replies
3
Views
262
Okay, probably a dumb question..but what does FTND stand for in the FT SE architecture? FTAC - is FactoryTalk Admin Console FTH - is FactoryTalk...
Replies
11
Views
1,102
Anyone ever heard of CTC PLC's? Not even sure if they're around anymore, I think they source out of Hopkinton MA but I could be wrong. They seem...
Replies
1
Views
1,651
Back
Top Bottom