FactoryTalk View Alarm History Problem
pampoon
Feb 2014
Louisiana
I have an SE application set up with alarming through SQL. The data that I am pulling in is coming through radio shot from a few miles away and every time the comms drop out for a second, the Alarm History logs "Alarm fault: Alarm input quality is bad" and then "Alarm fault cleared: Alarm input quality is good" when the comms come back up. This happens hundreds of times a day and it is filling the Alarm History up which makes it hard to find actual alarms. I have tried adding filters to clear out the nuisance alarms, but to no avail. This is my first time dealing with the 7.0 version of FTView so I'm still catching on to it, but does anyone know of a way to rid the History of these alarm input logs?
Picture for clarity:
Solution
This setting is under policies in FT Studio.
In your project navigation tree in Sutdio:
- Navigate to System -> Policies -> System Policies -> FT Alarm and Events -> System Settings
And check the box for "Only send changes in quality for active alarms to the alarm history log"
Hope this helps.
Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
141
Hi all. I´ve got a little problem with my FT View SE alarm window. On my PLC program, I have 200 SINT for alarms, in which every bit is for one...
186
Hello everyone, I am experiencing a strange issue with machine using a PanelView Plus 7 and a CompactLogix 1769 PLC. I am using FTView ME V13...
339
Hi All, I'm currently designing a faceplate for an analog input object, and I'm trying to create an alarm tab with an Alarm and Event Summary...
446
Hello! In FTView SE 13.00 for the AlarmEventSummary1 object I need to add the filter Alarm Name LIKE % %. In the field % % I want to pass a...
550